[time-nuts] Re: GPSDO Control loop autotuning
Erik Kaashoek
erik at kaashoek.com
Thu Apr 21 09:00:02 UTC 2022
Hi Tobias,
Using the excellent material found here:
https://nbviewer.ipython.org/github/rlabbe/Kalman-and-Bayesian-Filters-in-Python/blob/master/table_of_contents.ipynb
I went ahead and implemented the first order filter as described in
chapter 8.
The simulation was changed to use a real recorded PPS as measurement
noise and a real recorded TIC of a TCXO as the to be estimated data and
a Vtune steering an added frequency
The STDEV of the PPS was 5.6e-9
The kalman filter predicts the phase and frequency fairly well
STDERR of phase is 4e-9
STDERR of freq is 1.75e-9
The loop was then closed with a PI controller tasked to minimize the
phase error.
Tuning was a bit of a problem but the current performance is
STDEV phase error 1.25e-8
STDEV frequency error 1.2e-9
Unfortunately the resulting ADEV is still worse compared to a well tuned
PI controller acting directly on the TIC of the TCXO.
More work to do
Erik.
On 21-4-2022 9:44, Pluess, Tobias via time-nuts wrote:
> Hi Erik,
>
> yes I also found this webpage, and the examples are good.
> I had the exact same idea as you, except I thought that the model for the
> VCO output is either phase only or phase and frequency. Yours is even a bit
> more sophisticated, thats quite cool!
> And yes, of course it will be possible to have a one dimensional filter,
> even if your state space equations have more than one state. However, in
> this case, A, B and C are a matrix and two vectors (sometimes also called
> F, G and H). But the output that is measured ("observed") is just scalar,
> i.e. 1D.
> I am not sure whether your state extrapolation is correct, I don't see it
> at the moment unfortunately. But I will think about it a bit more.
>
> To your question, about how to close the loop.
> Well. What do you do when you don't have the alpha-beta-gamma filter?
> you take your phase error readings and feed them into some sort of
> controller, for example a PID controller, do you.
> Now think of the alpha-beta-gamma filter (or also the Kalman filter) as
> some sort of "prefilter". (do you remember when you asked me why I
> prefilter my 1PPS measurements? :-D at that time, I had a 2pole IIR filter
> with adjustable time constant as prefilter). So you feed your actual 1PPS
> measurements into the alpha-beta-gamma filter, and the filter outputs the
> 1PPS measurements, but with noise mostly removed (hopefully!). Then, use
> this as the error signal for your controller.
>
> As how to choose the alpha, beta and gamma coefficients, you need to know
> the variance of your input signal. i.e. determine the standard deviation of
> the 1PPS readings and square that. I am not sure at the moment how to find
> the coefficients from the variance, but I believe somewhere in the
> kalmanfilter.net tutorial, there is an equation for it if I remember
> correctly.
> Also worth mentioning is the fact that some GPS modules also output an
> estimate of the timing accuracy. This can also be used as an additional
> input to calculate the coefficients and adapt them, as receiving conditions
> change.
>
> does that help a bit?
> I am unfortunately not yet so far as you, I have made some calculations
> using matlab, but I am not sure whether they are correct. I do see some
> filtering effect of the Kalman filter, though. (I used the Kalman filter,
> with the error covariance matrices, not the alpha-beta-gamma filter, like
> you did, but maybe this is a better idea!). Are you interested in sharing
> your excel sheet?
>
> thanks,
> best
> Tobias
> HB9FSX
>
>
>
>
> On Wed, Apr 20, 2022 at 1:18 AM Erik Kaashoek <erik at kaashoek.com> wrote:
>
>> Tobias,
>> Your Kalman post triggered me to study this "dummy" level introduction
>> to Kalman filters: https://www.kalmanfilter.net/
>> and now I'm trying to write the Kalman filter.
>> An example of a Kalman filter described in the link above uses distance,
>> speed and acceleration as predictors for a one dimensional Kalman filter
>> So I wondered if it would be possible to do the same for the phase, eg
>> use phase, frequency and drift in the prediction model and still have a
>> one dimensional model?
>> The Kalman filter thus uses the normalized phase as input (the measured
>> time difference between the 1 PPS and the 1 second pulse derived from
>> the VCO output) to predict the next phase, frequency and drift
>> p = phase
>> f = frequency (d Phase/d T)
>> d = drift (d Frequency / d T)
>> m = measured phase
>> with a 1 second interval between observations the state extrapolation
>> (or prediction) is
>> p[k+1] = p[k] + f[k] + 0.5*d[k]
>> f[k+1] = f[k] + d[k]
>> d[k+1] = d[k]
>> and the state update is
>> p[k] = p[k-1] + alpha*( m - p[k-1])
>> f[k] = f[k-1] + beta*(m-p[k-1])
>> d[k] = d[k-1] + gamma*(m-p[k-1])/0.5)
>>
>> In a small simulation (in excel) I used a VCO that initially is on the
>> correct frequency, after some seconds Vtune has a jump and after some
>> more seconds the Vtune starts to drift.
>> The Vtune of the VCO can have noise(system error) and the m can have
>> noise (measurement error).
>> The p,f and m nicely track the input values even when measurement noise
>> is added but after this I'm stuck as I do not yet understand how to
>> calculate the alpha, beta and gamma values from the observed measurement
>> error as the above website does not yet explain how to do this.
>> And I do not understand how to close the loop to either keep the phase
>> error or frequency error as low as possible.
>> So much to learn.
>> Erik.
>>
>> On 16-4-2022 22:44, Pluess, Tobias via time-nuts wrote:
>>> Hallo all,
>>>
>>> In the meantime I had to refresh my knowledge about state-space
>>> representation and Kalman filters, since it was quite a while ago since I
>>> had this topic.
>>>
>>> So I looked at the equations of the Kalman filter. To my understanding,
>> we
>>> can use it like an observer, and instead of using the phase error and
>>> feeding it to the PI controller, we use the output of the Kalman filter
>> as
>>> input to the PI controller. And the Kalman filter gets its input from the
>>> phase error, but we also tell it how much variance this phase error has.
>>> Luckily, the GPS module outputs an estimate of the timing accuracy, so I
>>> believe one could use this (after squaring) as the estimate of the timing
>>> variance, correct?
>>>
>>> I believe depending on how we model the VCO, we can get away with a
>> scalar
>>> Kalman filter and circumvent the matrix and vector operations.
>>> I tried to simulate it in Matlab, and it kind of worked, but I noticed
>> some
>>> strange effects.
>>>
>>> a) I made a very simple VCO model, that simulates the phase error. It is
>>> x[k+1] = x[k] + KVCO * u with u being the DAC code. If KVCO is chosen
>>> correctly, this perfectly models the phase measurements. I assumed the
>>> process noise is zero, and the 1PPS jitter contributes only to the
>>> measurement noise.
>>>
>>> b) from the above model, we have a very simple state space model, if you
>>> want to call it like this. We have A = 1, B=KVCO, C=1, D=0.
>>>
>>> c) in the "prediction phase" for the Kalman filter, the error covariance
>>> (in this case, the error variance, actually) is P_new=APA' + Q, which
>>> reduces in this case to P_new=P+Q with Q being the process noise
>> variance,
>>> which I believe is negligible in this case.
>>>
>>> d) in the "update phase" of the Kalman filter, we find the Kalman gain as
>>> K=P*C*inv(C'*P*C + R), and this reduces, as everything is scalar and C=1,
>>> to K=P/(P+R), with R being the measurement noise, which, I believe, is
>>> equal to the timing accuracy estimate of the GPS module. Correct? we then
>>> update the model xhat = A*xhat + b*u + K*(y-c*xhat), which simplifies to
>>> xhat=xhat + Kvco*u + K*(y-xhat). Nothing special so far.
>>>
>>> e) now comes my weird observation. I don't know whether this is correct.
>>> The error covariance is now updated according to P=(I-K*C)*P, this breaks
>>> down to P=P-K*P. I now observe that P behaves very odd, first we set
>> P=P+Q,
>>> and then we set P=P-K*P. It does not really converge in my Matlab
>>> Simulation, and I see that the noise is filtered somewhat, but not very
>>> good. It could also be related to my variances not being correctly set, I
>>> am not sure. Or I made some mistakes with the equations.
>>>
>>> Any hints?
>>>
>>> As soon as I see it sort of working in Matlab, I want to test it on my
>>> GPSDO. Especially the fact that I have an estimate of the timing error
>> (the
>>> GPS module announces this value via a special telegram!) I find very
>>> amazing and hope I can make use of this.
>>>
>>> best
>>> Tobias
>>> HB9FSX
>>>
>>>
>>>
>>> On Tue, Apr 12, 2022 at 11:23 PM glen english LIST <
>> glenlist at cortexrf.com.au>
>>> wrote:
>>>
>>>> For isolating noise, (for the purpose of off line analysis) , using ICA
>>>> (Independent Component Analysis) , a kind of blind source separation ,
>>>> can assist parting out the various noises to assist understanding the
>>>> system better . There are some Python primers around for it.
>>>>
>>>> fantastic discussion going on here. love it.
>>>>
>>>> glen
>>>>
>>>>
>>>> On 12/04/2022 6:42 pm, Markus Kleinhenz via time-nuts wrote:
>>>>> Hi Tobias,
>>>>>
>>>>> Am 11.04.2022 um 13:33 schrieb Pluess, Tobias via tim
>>>> _______________________________________________
>>>> time-nuts mailing list -- time-nuts at lists.febo.com -- To unsubscribe
>> send
>>>> an email to time-nuts-leave at lists.febo.com
>>>> To unsubscribe, go to and follow the instructions there.
>>> _______________________________________________
>>> time-nuts mailing list -- time-nuts at lists.febo.com -- To unsubscribe
>> send an email to time-nuts-leave at lists.febo.com
>>> To unsubscribe, go to and follow the instructions there.
>> _______________________________________________
>> time-nuts mailing list -- time-nuts at lists.febo.com -- To unsubscribe send
>> an email to time-nuts-leave at lists.febo.com
>> To unsubscribe, go to and follow the instructions there.
> _______________________________________________
> time-nuts mailing list -- time-nuts at lists.febo.com -- To unsubscribe send an email to time-nuts-leave at lists.febo.com
> To unsubscribe, go to and follow the instructions there.
More information about the Time-nuts_lists.febo.com
mailing list