[volt-nuts] Best way to measure micro Ohms
Dan Kemppainen
dan at irtelemetrics.com
Wed Sep 20 09:49:19 EDT 2017
Aluminum...
Even with everything done right, with approved hardware, aluminum wiring
will tend to 'creep' (Aluminum mushing out of the way of the lug screw
or clamp.
Just recently I checked the main lugs on my 150A garage sub panel, and
sure enough the neutral lug was loose. This was about 8 years after
installation, with virtually no use (only one circuit used for lights
until now.)
However I believe this is only a problem with the softer grades of
aluminum. If your enclosure were out of 7075, or 2024 my guess is you
wouldn't see aluminum creep at all. 6061-T6 or similar would probably be
OK also. It's the soft stuff that moves easily. They all form the oxide
layer, so that's still a problem...
In a pinch, I may be able to machine something, but shipping to there
from here is probably expensive...
Dan
On 9/20/2017 8:28 AM, volt-nuts-request at febo.com wrote:
> An aluminum electrical connection needs a few things to
> be reliable:
>
> 1) a "springy" fastener
> 2) mechanical precleaning
> 3) an oxygen blocking coating.
>
> In the US, aluminum conductors are allowed for certain
> usages. We used to allow 14 and 12AWG receptacle wiring,
> but too many houses burned down. The receptacles were
> redesigned for Cu or Al, but the codes remained stubbornly
> against the practice. A few more times where copper prices
> go through the roof, and the codes will change.
>
> For larger conductors, the wire, or bar, is brightened up
> with Emory paper, or a stainless steel (important!) brush,
> and then is covered with "Gorilla Snot", or some sort of
> NoAlOx grease. NoAlOx is a grease made of an oxygen
> resistant heavy oil, and a coarse emory grit. I like to
> again rough things up after the NoAlOx is liberally applied.
>
> Finally, the conductors are tightened to specified torque
> using a springy fastener... The springy fastener is often
> simply an ordinary fastener with a "Bellview Washer" stack
> to give it compliance.
>
> The big thing that makes high current aluminum joints
> fail is thermal expansion. If the fastener isn't springy,
> the aluminum expands from the heat, finds it cannot go
> in the direction of the tightened fastener, and flows
> elsewhere. When the joint cools, and the aluminum under
> the fastener shrinks, the joint is now loose, and will
> arc when current is once again applied, evaporating more
> aluminum out of the joint. Soon the fire department will
> be coming... if you are lucky.
>
> NoAlOx prevents this issue, if you use a springy fastener.
>
> -Chuck Harris
More information about the volt-nuts