[time-nuts] PLL on FPGA
Pablo Alvarez Sanchez
Pablo.Alvarez.Sanchez at cern.ch
Tue Aug 7 14:52:48 UTC 2007
> -----Original Message-----
> From: Magnus Danielson [mailto:magnus at rubidium.dyndns.org]
> Sent: Monday, August 06, 2007 8:49 PM
> To: Pablo Alvarez Sanchez
> Cc: time-nuts at febo.com
> Subject: Re: [time-nuts] PLL on FPGA
>
> From: "Pablo Alvarez Sanchez" <Pablo.Alvarez.Sanchez at cern.ch>
> Subject: RE: [time-nuts] PLL on FPGA
> Date: Mon, 6 Aug 2007 18:49:23 +0200
> Message-ID:
> <42A60383A3EA19429E22C122E276B2F48C4AFC at cernxchg44.cern.ch>
>
> Is your sample/message rate that of 8 kHz?
My sampling rate is not constant. I wait until I detect a 3 ticks of the
500kHz clock and then start sampling.
After 2048 samples I do an average (first order CIC) and pass this value
to the PI. The PI operates at variable ratio of ~250Hz if there are no
data or 125Hz if there are data. The fact of not having a regular trafic
on the cable may also affect a bit to the final performance.
> > > > The jitter I measured with a good scope is ~120ps between
> > > two modules
> > > > for several minutes.
> > >
> > > Peak-to-Peak or RMS? For pure noise measures only use RMS
> values!!!
> >
> >
> > This is RMS
> It is high then. You should be able to get better performance.
>
Thanks for the info. This is really what I wanted to know. I will work
on this point.
What do you think I should be able to obtain?
Do you think a bang-bang phase detector and setting a good reference
point should do a better job?
> Cheers,
> Magnus
>
Cheers
Pablo
More information about the Time-nuts_lists.febo.com