[time-nuts] AC Connector On HP 5061B
Steve Rooke
sar10538 at gmail.com
Thu Oct 2 19:02:27 UTC 2008
2008/10/3 Brooke Clarke <brooke at pacific.net>:
> It's not clear to me how 230 VAC countries handle that problem? If they also
> use the same transformer but only bring in the 230 VAC then neither side of the
> line is near ground potential.
In 230/240 VAC the neutral side of the transformer output is earthed
at the transformer end. So breakdowns in the transformer go direct to
earth at the distribution transformer itself. At the customer end you
will find a small voltage at the neutral terminal due to the current
running down the resistance of the conductor back to the transformer.
As this is not a balanced supply, outlets have specific connections to
each pole of the mains and earth. The earth connection is made
locally, usually bonded to the incoming water main.
73
Steve
--
Steve Rooke - ZL3TUV & G8KVD
Omnium finis imminet
More information about the Time-nuts_lists.febo.com