[time-nuts] Power Back-up
Hal Murray
hmurray at megapathdsl.net
Sun Aug 9 20:28:25 UTC 2009
> Keep in mind that the batteries are not the only thing on small cheap
> Domestic UPS's that are rated for minutes. Same goes with their
> electronics, Heatsink etc.
If you are interested in times measured in hours, you will be running a
typical small UPS at well below full load.
For example, if full load is 5 minutes, 2 hours will be 5%.
That's assuming time*load is linear. From what I've lower loads load are
more efficient. For example:
Typical Backup Time at Half Load 15.9 minutes (250 Watts)
Typical Backup Time at Full Load 4.6 minutes (500 Watts)
That's for an APC SUA750 from:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA75
0&total_watts=50
Somebody pointed out that low loads are inefficient. That doesn't match the
numbers I'm seeing, Maybe I'm not looking at low enough loads. From their
chart:
Watts * minutes
50 * 103 = 5150
100 * 50 = 5000
250 * 15.9 = 3975
500 * 4.6 = 2300
I wonder where the knee is. 20w? 10w?
That's also from the data sheet rather than measured. It probably assumes a
new battery.
--
These are my opinions, not necessarily my employer's. I hate spam.
More information about the Time-nuts_lists.febo.com
mailing list