[time-nuts] GPSDO control loops and correctingquantization error
Bob Camp
lists at rtty.us
Fri Sep 14 20:17:48 UTC 2012
Hi
In the case of some systems, "long term" may only cut in past a few hours.
In the case of a Rb, it may be a few days.
If the reference "sees" room temperature, it's going to need very good
temperature stability for full 32 bit resolution. Something in the 0.2 ppb
/ C range...
Bob
-----Original Message-----
From: time-nuts-bounces at febo.com [mailto:time-nuts-bounces at febo.com] On
Behalf Of Bruce Griffiths
Sent: Friday, September 14, 2012 3:50 PM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] GPSDO control loops and correctingquantization
error
Azelio Boriani wrote:
> Also you need a super ultra fantastic voltage reference for a 32bit DAC.
>
Not really, the reference only needs to have low noise and good short
term stability.
Long term drift in the reference voltage will be corrected by the
feedback loop.
> Anyway, yes, in my GPSDO the controller has 3 levels: at startup is fast,
> then slow and then very slow. The levels trigger when the precision
> estimate is 10E-9 and 10E-11. If you have a resolution of 10nS then take
10
> averages and your resolution will be 1nS and so on.
However the noise associated with the timing resolution doesn't average
down so quickly.
If such noise is random than at best it is reduced by SQRT(10) by
averaging 10 measurements.
There is no real substitute for lower noise, higher resolution measurements.
> When I switch level,
> the number of averages is increased too but this leads to a slower DAC
> update rate. This is the problem: now I'm trying to figure out if the
> corrective action can be "predicted" (Kalman filtering) and applied at the
> same speed.
>
Bruce
> On Fri, Sep 14, 2012 at 8:52 PM, Chris Albertson
> <albertson.chris at gmail.com>wrote:
>
>
>> On Fri, Sep 14, 2012 at 11:21 AM, Michael Tharp
>> <gxti at partiallystapled.com> wrote:
>>
>>
>>> Finally, do people think a 16 bit DAC is adequate or should I consider
>>> building a 32-bit one? I looked at a few designs when putting this
>>>
>> together
>>
>>> but decided to keep it simple until things were up and running.
>>>
>> Having a 32-bit DAC would give you enough range so that you could drop
>> in any OCXO you might have. But if you can have trimmer resisters to
>> selected for your specif OCXO then 16-bits should be enough. If it
>> were me, I'd want the DAC steps to be smaller than what the phase
>> detector can measure. Said another way a 32-bit DAC might
>> eliminate the need for scale and offset trimmer resistors.
>>
>> Chris Albertson
>> Redondo Beach, California
>>
>> _______________________________________________
>> time-nuts mailing list -- time-nuts at febo.com
>> To unsubscribe, go to
>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
>> and follow the instructions there.
>>
>>
> _______________________________________________
> time-nuts mailing list -- time-nuts at febo.com
> To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts