[time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp
Chris Albertson
albertson.chris at gmail.com
Thu Nov 27 01:02:54 UTC 2014
You really do have to bond the two of them. The VERY best way is to dig a
trench all the way around the building and install a loop of wire, #8 at
least (although I use much larger wire after the time and money to dug a
trench.) This wire connects the rods and the water system. While a full
loop is best yo can simply run a wire to the building's service entrance
but I think code requires these wires to be "protected" by any of several
methods.
You have to connect the grounds because otherwire you have a problem where
indoors there are two different ground potentials. The Earth is just that
way, there is or may be a voltage potential between two spots. There WILL
be a difference during a lightening strike.
On Wed, Nov 26, 2014 at 2:54 PM, Hal Murray <hmurray at megapathdsl.net> wrote:
>
> albertson.chris at gmail.com said:
> > The ground rod needs to be bonded to the rest of the building ground
> system.
>
> How do I do that effectively if the power goes in the front of the building
> and the antenna is on the back?
>
>
>
> --
> These are my opinions. I hate spam.
>
>
>
> _______________________________________________
> time-nuts mailing list -- time-nuts at febo.com
> To unsubscribe, go to
> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
> and follow the instructions there.
>
--
Chris Albertson
Redondo Beach, California
More information about the Time-nuts_lists.febo.com