[time-nuts] lightening protection of a GPSDO system / optical isolated distribution amp
Chris Albertson
albertson.chris at gmail.com
Thu Nov 27 01:23:07 UTC 2014
On Wed, Nov 26, 2014 at 4:03 PM, Jim Lux <jimlux at earthlink.net> wrote:
> On 11/26/14, 2:14 PM, Chris Albertson wrote:
>
>> You CAN (almost) lightening proof your system. The trick is to give
>> lightening a low impedence path to grind at very opportunity.
>>
>> Start with the antenna mast and call. Use iron pipe for the mast and feed
>> the antenna cable down the center of the pipe. Place two large ground
>> clamps on this pipe and connect a large diameter wire that takes a
>> straight
>> path to a group rod. This will go a long way to diverting energy to
>> ground because high voltage likes to flow on the outside of a conductor
>> which would be the pipe and not so much the antenna cable.
>>
>
> Not so much high voltage, as AC and skin effect. However, bear in mind
> that lightning has a rise time of a microsecond or so: you can think of it
> having a fundamental of 300-500 kHz (e.g. the first quarter cycle of a
> sinewave), with most of the power below 1MHz.
>
> Skin depth at 1 MHz in copper is 0.065mm.
>
> In iron (using conductivty of 9.6 and relative mu of 1000) skin depth is
> 0.005 mm
>
> So, steel/iron pipe is a terrible conductor for a lightning impulse,
> compared to that nice copper coax next to it, or inside it.
>
Really? What you care about is the impedance, not the depth of the skin
effect. Also not the the coax is NOT exposed to the environment. Tacitly
the coax comes out from the user side of the antenna, so it never sees
daylight. The current flows in that first .005mm of steel. Running the
coax down the side of the pipe would be a really bad idea.
>
>
>
>> The ground rod needs to be bonded to the rest of the building ground
>> system.
>>
>> Then the antenna cable passes through a metal bulkhead with a bulkhead
>> connector and all this is also grounded. After this is might be a high
>> voltage e on the center conductor. Use an "lightening arrester that is
>> bolted to the bulkhead.
>>
>
> From a electrical code standpoint, a grounded bulkhead connector isn't
> compliant: you need one of those clamps that attaches to the shield in a
> quasi permanent way. I'm not sure of the entire rationale, but I think it's
> because connectors can become disconnected, but bolted connections less so.
>
>
>
>> At this point you are reasonably safe. Remember that Ethernet is always
>> gavalically isolated by transformers
>>
>
> Which won't necessarily stand off a 10 kV lightning impulse. and, of
> course, a common mode impulse carried on both wires of a pair might couple
> via either capacitance, or more likely, through magnetic fields.
>
> the ethernet galvanic isolation does a nice job dealing with the 10s or
> maybe 100V common mode issues, and protects the network if there is an
> internal short in a piece of equipment connected to the network.
>
> Of course, with the increased prevalence of Power Over Ethernet, some
> implementations of which are, shall we say, sketchy, that PoE system might
> be a dandy conductor of transient energy. For instance, a point to point
> microwave network terminal up on a mast running power for the circuit up
> the network cable.
>
>
>
> _______________________________________________
> time-nuts mailing list -- time-nuts at febo.com
> To unsubscribe, go to https://www.febo.com/cgi-bin/
> mailman/listinfo/time-nuts
> and follow the instructions there.
>
--
Chris Albertson
Redondo Beach, California
More information about the Time-nuts_lists.febo.com
mailing list