[time-nuts] A Research Proposal
jimlux
jimlux at earthlink.net
Mon Jul 8 23:14:56 UTC 2019
On 7/8/19 3:11 PM, Hal Murray wrote:
>
> glenlist at pacificmedia.com.au said:
>> I think people getting confused with the phase of measured current to the
>> voltage .
>
> No, we have been discussion the phase angle between 2 geographically separated
> locations connected by a power line.
>
> Consider the simple case of a generator, 100 miles of line, and then a light
> bulb. The voltage at the light bulb will be delayed by the speed of light.
> That delay can be expressed as a fraction of a cycle and converted to a phase
> angle.
>
> It gets much more complicated if you have multiple generators, multiple loads,
> and various transmission lines, and even more complicated when you turn things
> on and off.
The transmission line is decidedly not Velocity Factor =1.0
A typical propagation constant might be j0.0018/mile
about 5500 km/wavelength at 60 Hz.
Free space propgation delay for 5500 m is 18.5 milliseconds - compared
to 16.67 millisecond period of 60Hz. A velocity factor of about 90%
(that's for an example I found for 765 kV, using Tern conductors, in
bundles of 6
http://home.engineering.iastate.edu/~jdm/ee552/Transmission.pdf
)
>
>
More information about the Time-nuts_lists.febo.com