[time-nuts] Power glitch - Sat morning
Tim Shoppa
tshoppa at gmail.com
Tue Mar 31 12:43:44 UTC 2020
Hal, were there any storms or maybe just drenching rain in your area
Saturday AM? Fallen trees, drooping branches, and line crosses all go
together.
5 seconds is a very common value for circuit breaker reclosers as faults
either clear themselves or are isolated.
Tim N3QE
On Tue, Mar 31, 2020 at 1:24 AM Hal Murray <hmurray at megapathdsl.net> wrote:
>
> A while ago, I clean things up so that my system that monitors the line
> frequency was running off a UPS while watching the non-UPS line. I looked
> at
> some graphs. It seemed to be working. I moved on to other things.
>
> Last Sat morning, it got tested. Here is the graph of that area:
>
> http://users.megapathdsl.net/~hmurray/time-nuts/60Hz/60Hz-2020-Mar-28.png
>
> It's pretty obvious that power was off for 10 seconds, but what are the 2
> points in the middle?
>
> Below is the raw data from around that time. The second column is
> seconds-this-day. The samples are 10 seconds apart, grabbing time and
> count
> from the previous cycle. The 3rd column is the time and the 4th column is
> the
> count of cycles since started. The last column is the number of cycles
> since
> the previous sample. The next to the last column is the time since the
> last
> sample.
>
> 58936 60238.841 1585413838.824846 184208171 9.998426 600
> 58936 60248.843 1585413848.839454 184208772 10.014609 601
> 58936 60258.845 1585413858.837680 184209372 9.998226 600
> 58936 60268.846 1585413868.835009 184209968 9.997329 596
> 58936 60278.857 1585413878.849946 184210296 10.014937 328
> 58936 60288.867 1585413888.865095 184210897 10.015149 601 <==
> 58936 60298.876 1585413898.862521 184211146 9.997425 249
> 58936 60308.877 1585413908.876564 184211747 10.014044 601
> 58936 60318.888 1585413918.873961 184212347 9.997397 600
> 58936 60328.893 1585413928.888983 184212948 10.015021 601
>
> The marked line is a typical sample. The one after is is only 249 cycles
> in
> 10 seconds. The 2 lines above are both short.
>
> I'm pretty sure what happened is that there were two 5 second dropouts
> 10-15
> seconds apart. The first one just barely overlapped the end of a sample
> period: 596 cycles rather than 599, 600, or 601. Note that the last dot
> on
> the top line is slightly below the rest of the line.
>
> The second dot of the middle pair is the marked line.
>
>
> --
> These are my opinions. I hate spam.
>
>
>
>