[time-nuts] Re: Catching range of GPSDO
Bob kb8tq
kb8tq at n1k.org
Fri Mar 4 00:16:46 UTC 2022
Hi
> On Mar 3, 2022, at 3:36 PM, Erik Kaashoek <erik at kaashoek.com> wrote:
>
> The GPSDO I'm building started with frequency locking but now I'm adding
> phase locking so the time stamping counter can be on GPS time.
> A first version works with a PI controller setting the vc-tcxo Vtune DAC
> based on the phase difference of the 10 MHz with the PPS phase. Due to
> tolerances the tcxo frequency range is big and is set by a 16 bit DAC where
> 1 bit is about 2e-11 frequency change.
Take a look at just how good the LSB ( or maybe even LSBâs ⦠) on your
DAC really are. Some are not all that great and others are quite impressive.
Cost is indeed part of that. Summing a pair of lower resolution parts often
turns out to be pretty cost competitive.
With 2^16 steps a LSB of 2x10^-11 (and perfect linearity) you would get
a 1.3 ppm tune range. If itâs symmetric you would get +/- 0.65 ppm. That
probably is not âenoughâ to compensate for much aging on a low cost
TCXOâ¦..
> Once the DAC value is close to the correct frequency the loop catches
> nicely but if the setting is far off catching takes a long time.
> A possible solution is to use the frequency error to set the DAC close to
> the optimal frequency for catching.
> Speed of catching is important as the design is intended to only be
> switched on when needed.
> Does anyone have pointers to info on how to do quick catching in such a
> control loop?
The ânormal answerâ is to use a sequence of control loops. You start off with
a fast / wide band loop and then once it gets âgood enoughâ you go to a
somewhat narrower loop. Your state monitoring tells you when itâs got to an
adequately settled point and you step again. It is not uncommon to have
anywhere from a few to a dozen or so of these steps.
Bob
> Erik
> _______________________________________________
> time-nuts mailing list -- time-nuts at lists.febo.com -- To unsubscribe send an email to time-nuts-leave at lists.febo.com
> To unsubscribe, go to and follow the instructions there.
More information about the Time-nuts_lists.febo.com